Any tips on what the reverse power settings should look like- or what to consider?
Basically I am contemplating this as a last resort backup if you were to loose bus bar protection. Ie, 345 to 115kv substation with bus bar protection disabled. A bus fault on the 345kv side would be cleared via zone 2, but how would you get the interconnecting 345-115kv transformers to trip their breakers? Unless of course someone believes ANSI 21 (step impedance) would be better.
Basically I am contemplating this as a last resort backup if you were to loose bus bar protection. Ie, 345 to 115kv substation with bus bar protection disabled. A bus fault on the 345kv side would be cleared via zone 2, but how would you get the interconnecting 345-115kv transformers to trip their breakers? Unless of course someone believes ANSI 21 (step impedance) would be better.