Who are "they"? Phil
If "they" are the relay mfg, then ask "them" if "they" know about the probability of such maloperation!
Phil
Who are "they"? Phil
Who are "they"? Phil
Normally a 345kv (or 115kv) bus fault is cleared via bus bar differential protection which opens all the breakers connected to that bus. But picture a scenario where the bus bar protection is out of service (or fails)- you need a last resort backup. For 345kv lines entering the station the last resort for a fault on the 345kv bus bar will be cleared via Zone 2 step distance at the remote substations. However, Id like to have some type of means to remove the transformers.
No back up protection to differential protection? A restricted earth fault protection may so serve. In fact, one is back up protection to the other.
That is the question
is there ANY generation on the 115?
is it directly on the 115? Gen step up to 115
need a one-line showing combined capacity on each bus
I agree that an OL is needed for further discussion since your schemes have been a bit atypical in the past. For a fault on the 345kV t-line, the local distance relays (w/ comm trip) would clear. My guess is that there would also be some type of breaker failure scheme because of the 345kV level. For another backup layer, the xfmrs would have simple overcurrent in addition to the typical differential. For an additional backup layer, the lowside 115kV bank breaker relays could use a reverse distance element to look through the xfmr for faults on the 345kV side and trip after a 60-75 cyc delay. Since this element would be looking trough the xfmr, you could set the MTA to 90 and avoid any load encroachment issues for times when you want the 115kV to source the 345kV side. A lot depends on if most of the gen is on the 115 or 345 side.
If you're referring to the 345kV bus bar, I would be surprised if there is not a primary and backup bus diff. Per NERC guidelines and most utility policy, I don't think you can simply disable bus diff protection these days. There are many times when I've seen a cleared bus when enabling and disabling the bus diff. For a primary and backup bus diff relay, if the relay needs to be PM'd then one relay can be taken out at a time for testing. An added layer, is the Zone 2 of the remote end. Another added layer, is a Zone 3 reverse of the local line relays. They can be set to see through the xfmr(s) to the lowside.
Can you sketch a single line and show the fault that would cause this to happen?
thnx
I agree that an OL is needed for further discussion since your schemes have been a bit atypical in the past. For a fault on the 345kV t-line, the local distance relays (w/ comm trip) would clear. My guess is that there would also be some type of breaker failure scheme because of the 345kV level. For another backup layer, the xfmrs would have simple overcurrent in addition to the typical differential. For an additional backup layer, the lowside 115kV bank breaker relays could use a reverse distance element to look through the xfmr for faults on the 345kV side and trip after a 60-75 cyc delay. Since this element would be looking trough the xfmr, you could set the MTA to 90 and avoid any load encroachment issues for times when you want the 115kV to source the 345kV side. A lot depends on if most of the gen is on the 115 or 345 side.
If you truly have a lowside (115kV) bank bkr on all the xfmrs then you can use a distance relay to provide backup protection for a 345kV bus fault. This relay has the added benefit of using a different set of CTs and PTs than the highside relays.
device 32 and 67 for me are not the same...