Note there was a change in 2014.
450.11(B) says : "A transformer shall be permitted to be supplied at the marked secondary voltage, provided that the installation is in accordance with the manufacturer?s instructions."
Basically means you can only "back feed" a transformer if the transformer is specifically intended for reverse wiring.[/QUOTE
I am glad to see this change - here is why.
Delta 480x 120/208 Wye if reversed is a delta on the secondary and would have to be corner grounded, I suspect there are many that are not.
Sq D and probably others make a step up transformer, delta by wye, which I have used.
I agree that there are likely many systems out there that are not grounded. I also believe there are many incorrectly installed SDS that do have a secondary neutral, or are basic two wire or three phase three wire that also are not installed correctly. Installers need to know what they are doing is the bottom line IMO.
Grid tied PV inverters are by their nature current limited to their published maximum output. As for inrush current to the transformer, that can only come from the service side when the disconnect is closed because the inverters will not fire up until they have seen stable and correct voltage on their output terminals for 5 minutes or so.
I'm not really all that familiar with PV equipment, but thanks for the info.