None of that has changed, if you have a secondary with no neutral that is still necessary, but it is saying you can't just take any transformer and supply it from whichever side is convenient for you, it must be intended to be "back fed" if that is what you are going to do.I don't have a 2014 as we are on the 2011. Isn't the option still there to either bond and ground a corner of the delta OR provide Ground Detectors?
What I have in quotations in post 6 is the entire 450.11(B), and it is a new section in 2014.