1.) NEC Section/Paragraph: 210.52(B)(1), including exception 1
2.) Proposal Recommends: [revised text]
3.) Proposal: NEC-2005 text reads:
210.70(A)(1), Exception No. 1 states that "in other than kitchens and bathrooms one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets." There is no evident reason why small appliance branch circuits cannot perform this function, as most cord-and-plug connected lamps do not constitute a large enough load to compromise the primary function of these circuits. As a minimum standard, permitting the small appliance circuit to perform this function would be preferable to installing a 15-ampere receptacle beside a 20-ampere receptacle, inviting a small appliance load to be connected to the 15-ampere circuit.
In addition, the last statement in 210.52(B)(1), exception 1, is not literally correct, as no general purpose branch circuit is defined in 210.70(A)(1), exception 1.
Hee hee hee...
[ April 03, 2005, 01:21 AM: Message edited by: georgestolz ]
2.) Proposal Recommends: [revised text]
3.) Proposal: NEC-2005 text reads:
Revise text to read:(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Exception No 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general purpose branch circuit as defined in 210.70(A)(1), exception No. 1, shall be permitted.
4.) Substantiation: The numerous references to other sections do not contribute to the effectiveness of this section, so omitting them will add clarity while not changing the substance of this section. The other sections are also effective without 210.52(B)(1) referencing them, as well.(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the branch circuits required by 210.11(C)(1) shall serve all wall, floor, and countertop receptacle outlets, and receptacle outlets for refrigeration equipment. One receptacle of duplex receptacle outlets installed shall be permitted to be switched per 210.70(A)(1), exception No. 1.
Exception No 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from another circuit for lighting purposes shall be permitted.
210.70(A)(1), Exception No. 1 states that "in other than kitchens and bathrooms one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets." There is no evident reason why small appliance branch circuits cannot perform this function, as most cord-and-plug connected lamps do not constitute a large enough load to compromise the primary function of these circuits. As a minimum standard, permitting the small appliance circuit to perform this function would be preferable to installing a 15-ampere receptacle beside a 20-ampere receptacle, inviting a small appliance load to be connected to the 15-ampere circuit.
In addition, the last statement in 210.52(B)(1), exception 1, is not literally correct, as no general purpose branch circuit is defined in 210.70(A)(1), exception 1.
Hee hee hee...
[ April 03, 2005, 01:21 AM: Message edited by: georgestolz ]