RGS Per Code

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Do these conduits from the CT/switch down to the switchgear(feeder tag 3000) have to be RGS by code? Thanks
 

Attachments

  • Capture.JPG
    Capture.JPG
    98.4 KB · Views: 0

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There are very few code rules that require rigid conduit, but that is often required by the project specs.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
One possibility is for masts supporting a service weatherhead. But that may also be just a POCO policy.
Possibly fire pump wiring?

Fire pump wiring inside the electrical room or inside the fire pump room can be MC. Outside those two spaces, GRC alone won't be sufficient to meet the 2-hour survivability requirement.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I still don't understand why PVC isn't used. Rigid gives a parallel neutral so it would seem like it is better to have pvc. I guess there have never been bad effects from the rigid so they still require and , no doubt it is stronger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I still don't understand why PVC isn't used. Rigid gives a parallel neutral so it would seem like it is better to have pvc. I guess there have never been bad effects from the rigid so they still require and , no doubt it is stronger
There are any number of parallel paths for the grounded conductor current on the line side of the service disconnect. I don't see the path created by the use of metallic service raceways as an issue. I have seen issues with the code required parallel path via the TV cable shield and via metal underground water piping systems.

In my opinion. PVC has two uses. Where there are very serve corrosive conditions or underground. I have never seen an exposed PVC installation that looked good after a year or two. Even with supports as required by the code, it sags.

In this area, the local codes only permit rigid for service conductors.
 