B bassil Member Oct 20, 2003 #1 We decided to change all the electrical conduit for our sort area from RGS to EMT. We currently do not install separate ground wires in our conduit system. Since we are going to use EMT, is a separate ground wire required by the NEC?
We decided to change all the electrical conduit for our sort area from RGS to EMT. We currently do not install separate ground wires in our conduit system. Since we are going to use EMT, is a separate ground wire required by the NEC?
dereckbc Moderator Staff member Location Plano, TX Oct 20, 2003 #2 Re: RGS vs. EMT conduit ground Not if you comply with 250.118, but I recommend one. [ October 20, 2003, 04:29 PM: Message edited by: dereckbc ]