T timecon Member Location Rhinebeck Ny Occupation Solar manager Today at 11:18 AM #1 Installed a 250kW natural gas generator. The 4" rigid conduits are risers from PVC conduit in the ground. Are the ridged conduits need to bonded to ground.
Installed a 250kW natural gas generator. The 4" rigid conduits are risers from PVC conduit in the ground. Are the ridged conduits need to bonded to ground.
hbiss EC, New York NEC: 2017 Location Little Falls, New York NEC: 2017 Occupation EC Today at 11:31 AM #2 Do they connect to the generator housing? -Hal
T timecon Member Location Rhinebeck Ny Occupation Solar manager Today at 2:48 PM #3 No, the conduits come up through conduit window.
hbiss EC, New York NEC: 2017 Location Little Falls, New York NEC: 2017 Occupation EC 49 minutes ago #4 Then you will have to put grounding bushings on them and run a bonding wire through them to the generator EG. -Hal
Then you will have to put grounding bushings on them and run a bonding wire through them to the generator EG. -Hal