Ridgid conduit bonding

timecon

Member
Location
Rhinebeck Ny
Occupation
Solar manager
Installed a 250kW natural gas generator. The 4" rigid conduits are risers from PVC conduit in the ground. Are the ridged conduits need to bonded to ground.
 
As Hal stated they need to be bonded. You use a single bonding jumper for all of the raceways or individual bonding jumpers.
 