right and wrong colored conductors for 480volts

Status
Not open for further replies.
All nicely said until you go to a plant thats numbers and not colors!

Some guys cant see different colors as well as most. Maybe thats why the Purple for B phase in some places.

I will always use Orange as a hi leg and as B phase on 480 unless the plant has something else in place.
 
jrannis said:
All nicely said until you go to a plant thats numbers and not colors!

Some guys cant see different colors as well as most. Maybe thats why the Purple for B phase in some places.

I will always use Orange as a hi leg and as B phase on 480 unless the plant has something else in place.

480 does not have a high leg.
 
The colors of conductors can be anything you want. The only time they need to be identified (color coded) is if you have conditions that fall under 200.6.D for grounded conductors and 110.15 / 230.56 for the high-leg.

So, the only colors that have to be are:

Green - Ground
White/Grey - Neutral
Orange - High leg on a Delta

I can't think or remember any other ones.
 
Chamuit said:
The colors of conductors can be anything you want. The only time they need to be identified (color coded) is if you have conditions that fall under 200.6.D for grounded conductors and 110.15 / 230.56 for the high-leg.

So, the only colors that have to be are:

Green - Ground
White/Grey - Neutral
Orange - High leg on a Delta

I can't think or remember any other ones.

Can the grounding conductor be black?
 
tryinghard said:
my point is there is no high leg on 480. :grin:

Are you sure?

The one and only time I've seen something different was on an old farm. I installed 3 new services on various places around the farm and two of them had one leg that measured 405 volts to neutral if I remember correctly. 480 between phases.:-?
 
Cow said:
Are you sure?

The one and only time I've seen something different was on an old farm. I installed 3 new services on various places around the farm and two of them had one leg that measured 405 volts to neutral if I remember correctly. 480 between phases.:-?

What color would a low leg be?
 
Status
Not open for further replies.
Top