I’m going to pushback hard on this issue using this string as a basis. We have literally hundreds of these already connected and wired up.
Many thanks to all!
Are you the contractor who did the installation?
It seems that you are in a tough position. You did an installation that is totally reasonable but violates a listing...and not because it is 'wrong', but because 'it has not been evaluated'. So the customer is totally in the position to say 'this is wrong, fix it', even though it is almost certainly a non-issue in reality.
I wonder just how much UL would charge to 'evaluate' the exact assembly of connectors and couplings you used?
-Jonathan