Where is this in the code article?
300.6 Protection Against Corrosion and Deterioration.
(A) Ferrous Metal Equipment. Ferrous metal raceways, cable
trays, cablebus, auxiliary gutters, cable armor, boxes, cable
sheathing, cabinets, metal elbows, couplings, nipples, fittings,
supports, and support hardware shall be suitably protected
against corrosion inside and outside (except threads at joints)
by a coating of approved corrosion-resistant material. Where
corrosion protection is necessary and the conduit is threaded
in the field, the threads shall be coated with an approved electrically
conductive, corrosion-resistant compound.
It is not particularly likely, but there is a risk with Teflon tape that you do not get reliable electrical connections across the joints.I have read that but is there was someplace that said you could not use thread sealant and Teflon tape type compound to seal joints, guess that is the question I am looking for the answer to.
I have read that but is there was someplace that said you could not use thread sealant and Teflon tape type compound to seal joints, guess that is the question I am looking for the answer to.
I have read that but is there was someplace that said you could not use thread sealant and Teflon tape type compound to seal joints, guess that is the question I am looking for the answer to.
you can make uber tight, the small space between threads can still allow water in, a little amount.Is joining together a vertical section of RMC with a coupling wrench tight enough to keep water out? (Especially if it's coming out the top of a panel)
It generally seals well enough that you will get more water inside as a result of condensation then that joint will ever leak.Is joining together a vertical section of RMC with a coupling wrench tight enough to keep water out? (Especially if it's coming out the top of a panel)
It generally seals well enough that you will get more water inside as a result of condensation then that joint will ever leak.
I have never in 35+ years ever seen Teflon Tape insulate a connection of threaded pipe.
There may be other issues of Teflon Tape useage, but insulating joints is a non-issue. Go ahead, try it.:thumbsup: Hand tightening does not count!
The Teflon Tape is actually Anti-Seize tape, allows taper pipe threads to rotate (therefore get closer) than with the same pipe wrench force on dry threads.
I propose if Teflon Tape and other pipe dopes are actually insulating sections of pipe, the NEC would have made us bond every section of pipe to ensure a grounded piping system of water, air, gas, etc.![]()
It generally seals well enough that you will get more water inside as a result of condensation then that joint will ever leak.
Interesting thought - Galvanized rigid water pipe is suitable for grounding electrode/portion of grounding electrode conductor and they are likely to use sealant of some sort on the threads....
IMO, making the connection wrench tight mashes threads together enough there is good electrical conductivity between male/female parts of the joint, the sealant just fills in any remaining gaps.
I won't disagree. How much difference between the amount of contact when comparing straight thread coupling with and without a sealant occurs IDK. The small end of the tapered pipe thread likely isn't making that great of contact either way. I still think there is good enough contact that the pipe is going to carry any fault current imposed on it by any contained conductors, not like you are ordinarily going to solely depend on a 1/2 RMC to carry enough fault current to trip a 600 amp breakerI think that the tapered water coupling makes a better metal to metal connection to the pipe eating a lot more teflon than a straight electrical coupling.