RNC above ground...

Status
Not open for further replies.

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I have looked at 352,RNC, and I can't find anything that would prohibit using this to run along the ground. This run will be around a flower garden along the privacy fence. I am unable to trench this due to the amount of tree roots in this area. This will be about a 30' run.

Have I missed anything here?
 
Though the ground would provide support of the conduit, it would not be secured. You would need to strap it to the fence. I agree schedule 80 should be used.
 
Keep in mind PVC has a large thermal expansion coefficient. 9" in a 100 degree change of temp. It will look like a noodle if you don't allow for it.
 