Romex Above the Third Floor

Anibal Castilla

New User
Location
Miami, FL
Occupation
Foreman
Hi Mike
Every body talk about Romex can’t be use above a third floor in any building, but I don’t find anything like that on the NEC, I ask AI and said that is an old rule already removed. Would you please clarify that for me.
Location Miami Florida
 
Yes this 3 floors limit was removed from the NEC many code cycles ago in the 2002 NEC.
 
Last edited:
As Infinity said, it was removed many cycles back but it came with trade offs. Read 334.10 and 334.12
 