Mark, take a look at 334.10(A)(1).
Bob,
I have to agree with Mark's comment here as the code is a permissive code and a statement that specifically permits NM to be installed in normally dry locations does not act to prohibit the use of NM in wet locations.
This is a fundamental problem with the code wording in a number of cases. The CMPs seem to think that the specific permission acts as a prohibition of all applications. There is no reasonable reading of a statement that says I can do something that leads me to believe that I can't do something different.
Did this get changed for 2008? I'm still on 2005 cause that's what my jurisdiction uses. I try not to buy the new code book until we're using it. Otherwise I just get confused.
Mark
This is thrusting the code right out of reality! :-? It flies in the face of 334.12(B)(4).Type NM is NOT prohibited in "wet locations".
This is nothing short of distorting the actual intent of this section to create a new meaning that supports the reasoning that "excessive moisture or dampness is not present in a wet location".:-?:-?The code says "not exposed or subject to excessive moisture or dampness".
:-?Only the AHJ knows t(w)hat this means. What is considered excessive?
Sure it does. Look under Location, Damp, Location, Dry, and Location, Wet on page 70-30 in Article 100 Definitions.Sorry, but my 2005 code does not talk about dry, damp or wet locations.
Deductive reasoning must come into play. "Damp" is subject to moderate degrees of moisture, not saturation. Therefore "saturation" would be excessive to a damp location which would make it a "wet" location, no longer a "damp" location. "Dry" is not normally subject to either of these conditions.It says "excessive dampness or moisture". What's excessive. A drop? A bucket? Under pressure? Who knows. That's my point. I'm not trying to distort the code. When does some amount of moisture become excessive? Is a Wet Location excessive?
No change to the definitions for 2008, but the wording at 334.12(B)(4) was amended from "Where exposed or subject to excessive moisture or dampness"('05) to the new wording "In wet or damp locations" ('08)Respectfully,
Mark
PS: Hopefully the other post was from the 2008 and this has been changed, but I don't have the book to check.
Sorry, but my 2005 code does not talk about dry, damp or wet locations. It says "excessive dampness or moisture". What's excessive. A drop? A bucket? Under pressure? Who knows. That's my point. I'm not trying to distort the code. When does some amount of moisture become excessive? Is a Wet Location excessive?
Respectfully,
Mark
PS: Hopefully the other post was from the 2008 and this has been changed, but I don't have the book to check.
"I may not be able to define wetness, but I know it when I see it!"I have yet to meet anyone who cannot clearly tell the difference between a dry location, a damp location and a wet location.