Well, it does, but I still take that to mean isolated sections of conduit where needed, and not a complete, box-to-box conduit system. But then, I'm weird that way.CEU said:Article 334.15 (B) says it can be done.
LarryFine said:Well, it does, but I still take that to mean isolated sections of conduit where needed, and not a complete, box-to-box conduit system. But then, I'm weird that way.
iwire said:You can take it that way but it is not what it says.
As the NEC is a minimum safety code what would be the justification of prohibiting NM in conduit systems?
I agree it is weird but I don't see the hazard.
No one bats an eye when we pull fire alarm cable in a raceway system.![]()
roger said:Until we know what the maximum length of a "section of cable" installed in a raceway is, the last sentence above covers all NM installations in a raceway unless the raceway offers no protection from physical damage.
infinity said:Try pulling 8-#10 solid conductors into a 3/4" EMT and tell me if that is harder or easier than pulling in a piece of 12-2 romex.
LarryFine said:Okay, and then you try pulling four 10-2 NM's in the same 3/4" EMT and tell me if that was harder than pulling the eight #10's.
Personally, I'd rather pull the 10's than the NM.
This issue isn't a problem there....there is no Article 334 in their code.Might be a Chicago thing.
LarryFine said:What if
It doesn't matter, a section is a part of the whole and if all on the NM is in the raceway, it is not a "section of cable"...it is the cable.The word "section" is not pertaining to the raceway as it is worded, it is referring to the cable.
don_resqcapt19 said:by the way the code according to Don would not prohibit the use of NM in raceways...it would require it.
LMAOdon_resqcapt19 said:by the way the code according to Don would not prohibit the use of NM in raceways...it would require it.
Yes, I believe it would.roger said:What if a frog had wings, do you think his butt would still bump the ground?
yeah when it was lifting the wings and not on the down stroke.So it would bounce boing,boing,boing.RIBIT,Boing,RIBIT.LarryFine said:Yes, I believe it would.