-NEC 2011
- Use the Example of the 50 A Range circuit
- 250.122 sizes Equipment Grounding Conductors (EGC) not Grounded (neutral) conductors
- 210.19(A)(3)Ex.2 allows the neutral conductor for household cooking appliances to be smaller than the ungrounded conductors (70% of the branch circuit rating, but not less than 10 AWG, i.e.
.70 X 50A = 35A).
-If the 50A Range branch circuit is wired with individual conductors in conduit with THWN (75C) or
THHN (90C) insulation, then: 310.15(B)(16) Ungrounded conductors = 8 AWG, Neutral conductor = 10 AWG, Equipment Grounding Conductor (EGC) = 10 AWG (T250.122).
-If an SE cable with 75C insulation is used, then conductors sizes would be the same.
Note: NEC 2008 required SE used in Interior Installations to follow NM rules including 334.80 Ampacity, i.e. 60C column in T310.16. NEC 2011 excludes SE from 334.80 Ampacity requirements.
- If an NM cable is used then from 60C column: Ungrounded Conductors = 6 AWG, Neutral conductor = 8 AWG, and EGC is still = 10 AWG.