14/4 is commonly stocked where I work, and has been for a number of years.
3 15a is the absolute bare minimum for 1800 sq ft
5 15a is the absolute bare minimum for 3000 sq ft
If thats the way you want to wire go ahead , thats the way mobile homes are wired
I use:
3 15a and 2 20a on 1800 ft
5 15a and 3 or 4 20a on 3000 ft
So when you say I don't use enough circuits, what do you base that statement on?
The way you were first describing how much you would put on a single circuit no matter if the bed rooms were 20x20 ,I didnt see how it could add up to enough circuits . If you use the minimum or more then it is legal. If you start adding can lights and other things the minimum will get quickly overloaded.
So when you say I don't use enough circuits, what do you base that statement on? Just because you do things different than me, therefore I must be doing it wrong.
You also claim my phone is ringing at all hours of the night from customers with tripped breakers. What do you base that statement on?
I've simply stated that certain installations will meet minimum code. You turn around and claim that's the say I do things.
14/4 is commonly stocked where I work, and has been for a number of years.
No, it has been deleted. However, that had nothing to do with the new requirement for neutrals in switch boxes. In the 2008 NEC, 200.7(C)(2) was a redundant section, because it provided a permission that was a subset of the permissions provided by 200.7(C)(1). This commonly caused people to read 200.7(C)(2) as a restriction on the permission in 200.7(C)(1), but that was neither a literal reading nor the code committee's intent, as indicated by their comments on the successful 2011 proposal to delete 200.7(C)(2).With this new requirement, is 200.7(C)(2) still in the '11?
200.7(C)(1) 2011 NEC said:(C) Circuits of 50 Volts or More. The use of insulation that is white or gray or that has three continuous white stripes for other than a grounded conductor for circuits of 50 volts or more shall be permitted only as in (1) and (2).
(1) If part of a cable assembly that has the insulation permanently reidentified to indicate its use as an ungrounded conductor by marking tape, painting, or other effective means at its termination and at each location where the conductor is visible and accessible. Identification shall encircle the insulation and shall be a color other than white, gray, or green. If used for single-pole, 3-way or 4-way switch loops, the reidentified conductor with white or gray insulation or three continuous white stripes shall be used only for the supply to the switch, but not as a return conductor from the switch to the outlet.
14/3 is available everywhere. Run power to the switch first, then 14/3 to the fan/light. Why bother taking power to the ceiling, then trying to either find 14/4 or cobble something up with 2 runs of 14-2?
Either that, or run power to the ceiling & leave it there, and install an RF-controlled fan/light. NOW look at how much NM you've saved!
I have no doubt that more & more supply houses will start to stock 14-4 very soon.
What do most people use the 14/4 for there ? Soon we will need it to send a neutral and hot from ceiling to switch box , and have a return hot for the fan and light.
4 conductor can be a money saver if used right.
There are 2 neutrals, a white and a white with a stripe, enabling two separate circuits, each with their own neutrals to be run in one shot, as opposed to 2 runs of 2 conductor.
14/4 does not have to whites. It only has one.
14/2/2 has two whites.
14/4 is commonly stocked where I work, and has been for a number of years.
What do most people use the 14/4 for there ? Soon we will need it to send a neutral and hot from ceiling to switch box , and have a return hot for the fan and light.
Wow, that was not in the 2011 Draft NEC I looked at, 200.7(C)(2) had just been totally deleted. But I see the change to 200.7(C)(1) is in the final 2011 NEC, due to a proposal by Mike Holt at the ROC stage. While I don't agree with the change, at least the new language is unambiguous, unlike the 200.7(C)(1)/200.7(C)(2) redundancy that was present in the 1999-2008 NECs.Article 200.7(C)(2) Nec 2008 is now 200.7(C)(1) NEC 2011 with some wording change.