Romex switch legs
raider1
Logan, Utah
Make sure that the remarked white is used as the supply to the switch and not the return to the lighting outlet.
Check out 200.7(C)(1).
Chris
busman
Northern Virginia
Master Electrician / Electrical Engineer
It seems silly that we must recolor the wire so it's no longer white, but we must still use it as the white wire. :roll:
I agree either it's white or it's not. Which is it. If we re-color it, what difference does it make which leg it is. Just stupid. I'd much rather have the black feed the switch and recolor the white to red. Any electrician would make more sense of that.
Mark
480sparky
Iowegia
200.7(C)(2) has got to be one of the most stupid additions to the Code.
Is there anyone who is qualified really going to pull out a switch, look at a black and a white wire hooked to it, and think, "Dang! This thing is going to create a dead short, what with putting the black and white together like that on a switch!"
jeremysterling
Austin, TX
Mark
Could make sense of it with a voltmeter, perhaps.
We are trying to avoid opening a fixture with only the supply conductors entering the fixture make up area (say through a pop-in bushing) and both wires coming into the fixture are white (with the black tape above the fixture in the 4/0 box). Two white wires equals break out the meter and hope for a ground or use your tic tracer to figure out the hot. It is easier to use the traditional and required method of re-identifying.
When the rule was explained this way to me, it made some sense.
LarryFine
Henrico County, VA
Electrical Contractor
If you think about it, most often with a 2-wire switch loop, the feed wire (white) is connected to one or more blacks, and that connection rarely needs to be disturbed in the future.
On the other hand, with the white as the return, the load would now have two white wires supplying it. While it should be obvious which white is which, the first method is fool-proof.
Okay, let's make that fool-resistant. ;)
LarryFine
Henrico County, VA
You'd be surprised. I once had an inexperienced helper who saw a white wire on a 3-way, and removed it from the terminal and connected it to the "other neutrals" in the box. :roll:
jxofaltrds
Inspector Mike®
Mike P. Columbus Ohio
ESI, PI, RBO
Chris
Agreed. I was told on this forum years ago that this was not true. By the master himself.
It is on the old forum so I can not find it.
Now does it apply to travellers also????
LarryFine
Henrico County, VA
In the sense that the white should only be used for the hot feed to the "farthest" 3-way, and the black and red as the travelers back, yes.
The one place the white as a switched wire or traveler is unavoidable is the light-and-power-between-the-switches scenario.
ceb58
Raeford, NC
code change
code change
Isn't this going to change in the upcoming 2011 code? You can no longer use the 2 wire switch loop due to the requirement of having to have the grounded conductor in the box with the switch.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
I think the idea behind this is not to have two white wires coming in to a light fixture
Yes but it isn't white if it is taped blacked. :) That is what others are saying. I guess it can be easy to tape the wrong wire. I have no problem with this code and I have done it this when for 25 years or more.
sameguy
New York
Master Elec./JW retired
This is a skilled trade, why we are making it a "job" is so anyone, read that cheap unskilled labor can do most of our work. My doctor told me he too is having the same problem in his skilled trade.