Ask for a code reference on why you need the disco
Sent from my SAMSUNG-SM-N920A using Tapatalk
There were many local attempts to add emergency shutdown to the PV array in years past. There was an AHJ in Temecula CA that was requiring a remote operated DC contactor on the roof and this was maybe 7 or 8 years ago. Now that RSS is in the code all these local attempts to introduce array isolation need to be removed but guess who needs to do that? Local PV installers need to push for it when the local versions of codes are updated.
In the case of Fresno, the ordinance was snuck in with other changes to the fire code. No justification was provided pursuant to state law, I'm honestly not sure why no one called them out on that.