Correct. but the output conductors need 150 amp OCPD if they are going to be 150 amp conductors.
I am not as sure as that as you seem to be.
The point of reduction to that OCD is a feeder tap. Two lines are effectively direct connected to the input in such a converter, so at very least you have on those two lines the equivalent of a 150 amp conductor directly tapped to one with 225 amps overcurrent protection. The "manufactured" phase may be somewhat inherently protected from overload just by the impedance of the converter - but NEC likely wouldn't recognize that as proper protection anyway.
Not having done rotary phase converters would I be correct in saying that you only supply three phase loads with them?