Would you consider wire pulling part of the rough in or only the boxes/conduits etc., essentially the infrastructure.
So your saying wires need to be pulled in raceways for rough inspection in your area?Rules here say for the rough inspection, all boxes made up, grounds connected, etc. Be hard to not run wire if grounds are to be made up.
That is with or without conduit. We can cover walls before rough if using conduit, but not cable methods.
TN Code wording in part:::::So your saying wires need to be pulled in raceways for rough inspection in your area?
Good to know, i'm currently doing a data center in MurfreesboroTN Code wording in part:::::
No wiring or raceways shall be concealed until it has been inspected and approved by the inspector......
When the initial (“rough-in”) inspection is conducted:
(a) All applicable circuit conductors and outlet boxes shall be installed;
(b) All joints shall be made;
(with exceptions)
I have run in to that, and it is ridiculous in my opinion. That means you have pretty much have the entire ceiling done as well. What is the logic in requiring that? We actually got the building official down and talked him out of it. We would have ground pigs installed in every box, but could pull wire later.TN Code wording in part:::::
No wiring or raceways shall be concealed until it has been inspected and approved by the inspector......
When the initial (“rough-in”) inspection is conducted:
(a) All applicable circuit conductors and outlet boxes shall be installed;
(b) All joints shall be made;
(with exceptions)
I'd much rather do as much rough work as I can when I don't have to be so neat and clean.I have run in to that, and it is ridiculous in my opinion.
(a) requirement to inspect conduit systems prior to covering....I have run in to that, and it is ridiculous in my opinion. That means you have pretty much have the entire ceiling done as well. What is the logic in requiring that? We actually got the building official down and talked him out of it. We would have ground pigs installed in every box, but could pull wire later.
And the wiring pulling goes much faster when you can actually see the conduits where the conductors are being installed.I'd much rather do as much rough work as I can when I don't have to be so neat and clean.
I'm thinking just about all of the wire stripping scraps I don't have to sweep or vacuum up.
Fish-tape pulling can easily damage the edges of the drywall around outlet box openings.
Same for WARules here say for the rough inspection, all boxes made up, grounds connected, etc. Be hard to not run wire if grounds are to be made up.
That is with or without conduit. We can cover walls before rough if using conduit, but not cable methods.
Sounds like that only applies to work that's being concealed. Walls and hard lidsTN Code wording in part:::::
No wiring or raceways shall be concealed until it has been inspected and approved by the inspector......
When the initial (“rough-in”) inspection is conducted:
(a) All applicable circuit conductors and outlet boxes shall be installed;
(b) All joints shall be made;
(with exceptions)
What about "Neat, workman-like jobs" and "Broom-clean every night?"I'm thinking just about all of the wire stripping scraps I don't have to sweep or vacuum up.
Huh?"Broom-clean every night?"
We're talking about inspection requirements, not specific job requirements that may be in a contract.Broom-Clean is (was) often in construction contracts-- "the work area will be kept broom-clean every night." In other words, low man on the totem pole would sweep the area, gathering the stripping scraps and wire tidbits and dumping them in the trash can to keep the area neat and tidy.
Nothing in writing that I'm aware of be we are allowed to break down portions of a rough, like basement separate, garage, etc. Also can get a ceiling rough inspection as sometimes they want to insulate before finishing lower areas.Sounds like that only applies to work that's being concealed. Walls and hard lids
Here a rough-in inspection is just that. Nothing above a grid ceiling is required to be installed for wall rough inspection.
Then above ceiling inspection has to be done before tiles get dropped in, and covers everything from the conduit and circuiting to fixture wires.
Final is for everything below ceilings.