Typically side in and side out is done using a auxiliary section. I have seen conduits run along the side for opposite end entry, but there is not a lot room on the bottom of fused switches to make the cable crossovers.I get it, but is there a side in side out? lol
Also this service switch will feed a seperate 2000 amp distribution section.
I asked the sales engineer for just 1 separate distribution section and he said it would not be possible and that a pull section is required since the distribution section has 3-600 amp switches.