Xd is the generator’s steady-state synchronous reactance, while Xd' is the generator’s direct-axis transient-reactance! These two parameters should have already been supplied by the machine builder. Starting VD is the LRA of a motor x Xd' or the cold load pickup of the load switched x Xd'.adindas said:C0uld anybody guide me the rule of Thumb to calculate voltage Dip at the standby generator terminals, following load switching.
I have read it is a fuction of subtransient and transient reaxtance of the Generator.
Thank you
Adindas
There is no rule of thumb. There is only OHM's Law. VD = amps x impedance.adindas said:Thank you for all who r taking time to answer my question.
If you could assist me top provid rule of thumb formula.
Let take for instance:
Standby generator Genset Rating: 1250 KVA
Transient Reactance Xd' (pu) = 15%
I use to start a load simultaneously with total of:
Starting KVA (sKVA)= 1300 KVA
Starting KW (sKW)=350 KW
What is likely to VD at the teminal when the generator picks up the load?
Thank you again for your time
Adindas