Rule of Thumb to calculate voltage Dip for standby Generator

Status
Not open for further replies.

adindas

Member
COuld anybody guide me the rule of Thumb to calculate voltage Dip at the standby generator terminals, following load switching.

I have read it is a fuction of subtransient and transient reaxtance of the Generator.
Thank you

Adindas
 
adindas said:
C0uld anybody guide me the rule of Thumb to calculate voltage Dip at the standby generator terminals, following load switching.
I have read it is a fuction of subtransient and transient reaxtance of the Generator.
Thank you
Adindas
Xd is the generator’s steady-state synchronous reactance, while Xd' is the generator’s direct-axis transient-reactance! These two parameters should have already been supplied by the machine builder. Starting VD is the LRA of a motor x Xd' or the cold load pickup of the load switched x Xd'.
 
IS there any formula ?

IS there any formula ?

Thank you for all who r taking time to answer my question.
If you could assist me top provid rule of thumb formula.

Let take for instance:
Standby generator Genset Rating: 1250 KVA
Transient Reactance Xd' (pu) = 15%

I use to start a load simultaneously with total of:
Starting KVA (sKVA)= 1300 KVA
Starting KW (sKW)=350 KW

What is likely to VD at the teminal when the generato psick the load?

Thank you again for your time

Adindas
 
adindas said:
Thank you for all who r taking time to answer my question.
If you could assist me top provid rule of thumb formula.
Let take for instance:
Standby generator Genset Rating: 1250 KVA
Transient Reactance Xd' (pu) = 15%
I use to start a load simultaneously with total of:
Starting KVA (sKVA)= 1300 KVA
Starting KW (sKW)=350 KW

What is likely to VD at the teminal when the generator picks up the load?

Thank you again for your time

Adindas
There is no rule of thumb. There is only OHM's Law. VD = amps x impedance.
In you example Impedance is 0.15. You will have to get the amps from the
starting KVA.
 