running boards in basement

As I recall the requirement for boring or running boards was originally for unfinished basements.
I remember them for receptacles and switches on block basement walls, and the cables were always stapled to the face of the board, not the edges.

I haven't been able to find an example pic yet, but we can all picture it.
 
True but If I am going the length of the house with several cables I am not doing all that drilling.
then you need to run them in some sort of chase, on running boards or in raceways. Ampacity adjustments do apply if you don't maintain spacing of small enough "bundles" in any of those methods.
 
then you need to run them in some sort of chase, on running boards or in raceways. Ampacity adjustments do apply if you don't maintain spacing of small enough "bundles" in any of those methods.
Some sort of chase. is like saying some sort of wire. the more i rescarch this the less i know. some one from the nec should address this !
 
Some sort of chase. is like saying some sort of wire. the more i rescarch this the less i know. some one from the nec should address this !
The conduit is cheap and easy though. This in 1 1/2. That is room for a bunch of residential circuits. And if you want to add a circuit it's big enough to just push a piece of NM through. How large is this circuit?

1769978197064.png
 
.... some one from the nec should address this !
It doesn't work that way...you can get a Formal Interpretation from the NFPA on a rule in the NEC but it is a long process, many months, and you must submit your question in a way that it can be answered "yes" or "no".
For subjective rules like this the only answer is the one from your AHJ.
 
I am running Romex on running boards screwed to the bottom edge of the floor joists. No need for derating they are not bundled. Where I do go through drilled holes in the joists I keep the # of single conductors below 8.
 
I am running Romex on running boards screwed to the bottom edge of the floor joists. No need for derating they are not bundled. Where I do go through drilled holes in the joists I keep the # of single conductors below 8.
can you post a post a pitcher please ?
 
It doesn't work that way...you can get a Formal Interpretation from the NFPA on a rule in the NEC but it is a long process, many months, and you must submit your question in a way that it can be answered "yes" or "no".
For subjective rules like this the only answer is the one from your AHJ.
My ahj is a moron . like many others !
 
Some sort of chase. is like saying some sort of wire. the more i rescarch this the less i know. some one from the nec should address this !
I could describe possibly several hundred ways you could build some sort of chase or I could go pretty basic and mention building a chase out of wood, metal, plastic, maybe masonry?
 
I didn't factor in fill because I don't know what the circuit/circuits are. But even at 2 1/2, it's still cheap enough

View attachment 2581724
Not talking about fill, talking about the required ampacity adjustment for more than 3 current carrying conductors. At five MN cables in the raceway, you need to use 12 AWG for 15 amp circuits and 10 AWG for 20 amp circuits, when NM is installed in a raceway for more than 24".
 
Yes, better to have more smaller pipes than one huge one. Derating makes a large pipe not very usable. A chase where you could nail cables and maintain separation. or nail in those NM cable support "trees" would be fine.
 
Not talking about fill, talking about the required ampacity adjustment for more than 3 current carrying conductors. At five MN cables in the raceway, you need to use 12 AWG for 15 amp circuits and 10 AWG for 20 amp circuits, when NM is installed in a raceway for more than 24".
That's good to know. I've done it but never with 5 circuits. It's always me cleaning up a NM mess someone did in a commercial structure or a barn and I'm just sleveing the existing conductors.

Lots of smaller commercial buildings around here are a mess of Romex and residential grade devices. They seemed to be kind of electrically backwards here up until recently. I can think of a couple of large pole barns that are in commercial use with single phase power, and done entirely in romex. Not sure how that flew with the AHJ. And I'm talking obvious commercial structures with their own service, not something in back of someone's house
 