Running EMT without offsets

Status
Not open for further replies.

BarryO

Senior Member
Location
Bend, OR
Occupation
Electrical engineer (retired)
Apparently I'm in the minority, but I'd just use the minnerelac clips if the offsets present a problem. (I don't see them being a problem.)
Yea I've used them for the same reason (to eliminate offsets).
 

garbo

Senior Member
Just about any time that I have to run two or more conduits will use unistrut. Had to supply single & 3 phase power to 12 machines that were in an older building that had what I call a 8" brick bump out every 25' . Because these runs consisted of 360 degrees in bends & really did not want to install pull box or C condulets went with standard 1&5/8" deep unistrut coming down wall and mounted two 1900 boxes on shallow 5/8" deep unistrut to prevent having to install an offset and not exceeding 360 degree in bends. Most supply houses only stock 1&5/8 & 13/16' deep unistrut so I always had some 5/8" on hand.
 