I have hooked up some equipment to a 112.5KVA transformer and the load is turning out to be more than I expected. On a 112.5KVA transformer, we are measuring an average load of 76KVA and a peak load of up to 85KVA.

Everything is working fine but how concerned should I be at running the transformer at 70-75% of its rated capacity? Any thoughts?
 
I have hooked up some equipment to a 112.5KVA transformer and the load is turning out to be more than I expected. On a 112.5KVA transformer, we are measuring an average load of 76KVA and a peak load of up to 85KVA.

Everything is working fine but how concerned should I be at running the transformer at 70-75% of its rated capacity? Any thoughts?

I would not be worried until I started running it at 110% or so. At 75%, it will probably barely be warm. if you can hold your hand on it, it is fine.
 
I have hooked up some equipment to a 112.5KVA transformer and the load is turning out to be more than I expected. On a 112.5KVA transformer, we are measuring an average load of 76KVA and a peak load of up to 85KVA.

Everything is working fine but how concerned should I be at running the transformer at 70-75% of its rated capacity? Any thoughts?
Unless the "some equipment" generates high harmonic content current. Is the xfm hot to touch?

ice
 
Even if you can't it may be fine. The surface temperature of some transformers can exceed 140?F when fully loaded.

I must admit I am curious just how oversized the OP thinks a transformer ought to be.

I am a fan of building in some room to grow but a transformer that is only 70% loaded has almost 50% spare capacity.
 
I must admit I am curious just how oversized the OP thinks a transformer ought to be.

I am a fan of building in some room to grow but a transformer that is only 70% loaded has almost 50% spare capacity.
Interesting comment. I can't comment on the OP's thoughts. However, I do exclusively industrial applications and I would say the initial loading is entirely design dependent.

Double ended subs are never over 50%, unless there is a loadshed scheme - which is really rare. Normal every day dry types up to 500KVA are rarely loaded over 80%. Special stuff, like 100kva 480/277 grounded, or 225kva (or smaller) 208/120 are rarely loaded over 75%.

So, I must admit I am curious, just how undersize do you think a transformer ought to be? :)

ice
 
It.

Double ended subs are never over 50%, unless there is a loadshed scheme - which is really rare. Normal every day dry types up to 500KVA are rarely loaded over 80%. Special stuff, like 100kva 480/277 grounded, or 225kva (or smaller) 208/120 are rarely loaded over 75%.



ice

Your application is design dependent loading above 50% would defeat your redundancy.

In Washington DC (and most places I have worked) a typical office building design has a transformers operating at or less than 30%
 
temp rating should be on nameplate

temp rating should be on nameplate

Even if you can't it may be fine. The surface temperature of some transformers can exceed 140?F when fully loaded.

Nameplate will tell temp rise rating; it varies based on design. 150C (300F) is common design max temp for full load temp altho I hate to see it that high. Most xfmrs today use 220C insulation system. Most xfmrs of this size we sell probably sit at 140F idle.
 
I have a notion that Jim Dungar might not agree.
From memory, I think he came up with a figure of 30% loading being the target best efficiency point for some transformer directive/guide.
Science not withstanding, my opinion does not matter.

The US government enacted a law (Public Law 109-58 of the Energy Policy of 2005) that required transformers after 2007, to be designed with specific minimum efficiencies determined based on: (1) no-load losses at a temperature of 25?C and (2) load losses at a temperature of 75?C and 35 per cent of nameplate load.

The industry refers to these transformers as being per NEMA TP-1
 
Science not withstanding, my opinion does not matter.

The US government enacted a law (Public Law 109-58 of the Energy Policy of 2005) that required transformers after 2007, to be designed with specific minimum efficiencies determined based on: (1) no-load losses at a temperature of 25?C and (2) load losses at a temperature of 75?C and 35 per cent of nameplate load.

The industry refers to these transformers as being per NEMA TP-1
Yes. I should have checked then I wouldn't have dropped the 30% goolie.
At least I got your name right.
Does that go some way to mitigating my gaffe?
:)
 
Science not withstanding, my opinion does not matter.

The US government enacted a law (Public Law 109-58 of the Energy Policy of 2005) that required transformers after 2007, to be designed with specific minimum efficiencies determined based on: (1) no-load losses at a temperature of 25?C and (2) load losses at a temperature of 75?C and 35 per cent of nameplate load.

The industry refers to these transformers as being per NEMA TP-1

But these are newer transformers?
 
Science not withstanding, my opinion does not matter.

The US government enacted a law (Public Law 109-58 of the Energy Policy of 2005) that required transformers after 2007, to be designed with specific minimum efficiencies determined based on: (1) no-load losses at a temperature of 25?C and (2) load losses at a temperature of 75?C and 35 per cent of nameplate load.

The industry refers to these transformers as being per NEMA TP-1

of course general purpose distribution xfmrs built after 1/1/2007 must meet these specs, but it does not change physics: it is seldom that MAX efficiency happens at such a low 35% load level. so do not think 35% load level is now the default highest efficiency point - it is not. also seldom does max efficiency happen at 100% load - most of the time is is around 75-80% load. but the difference is seldom more than a couple % at most from no load to full load so of little concern.
 
Yes. I should have checked then I wouldn't have dropped the 30% goolie.
At least I got your name right.
Does that go some way to mitigating my gaffe?
:)

30-35% who's counting. The real point is that it is a federal law, not a matter of an ideal world, designating the design criteria.
 
The real point is that it is a federal law, not a matter of an ideal world, designating the design criteria.
But look at it, it just says that the efficiency at 35% load must meet some number ... and I'd bet that the TIME AVERAGED load on a general purpose transformer is in that range ...

It does not say (from what was written, I did not dig into the actual law) that the efficiency must be maximum at a 35% load.
 
Interesting comment. I can't comment on the OP's thoughts. However, I do exclusively industrial applications and I would say the initial loading is entirely design dependent.

Double ended subs are never over 50%, unless there is a loadshed scheme - which is really rare. Normal every day dry types up to 500KVA are rarely loaded over 80%. Special stuff, like 100kva 480/277 grounded, or 225kva (or smaller) 208/120 are rarely loaded over 75%.

So, I must admit I am curious, just how undersize do you think a transformer ought to be? :)

ice

I don't personally care how loaded it is. It is a design decision. It just seemed odd that the OP seemed to be worried that it was loaded at 70%. I would not give that a second thought.
 