- Illinois
- retired electrician
Re: Same circuit fed twice
Joe,
Don
Joe,
As soon as you tie the circuits together there are two paths for the current. The current will flow on both paths to the load(s). The division of current on each breaker will be a function of the impedance of the paths and will not result in a 50%/50% split, but the load currents anywhere on this circuit will have to far exceed 20 amps for the breakers to trip.IMO this is still a 20amp circuit that will trip when 20amps is exceded
Don