Would GFCI protection be required for an indoor dry sauna.
It’s located in an unfinished basement. It’s hardwired with a 6-2 SO cord and a disconnect.

It is a 9 KW 240 V unit that is being housed inside a homemade cedar enclosure.

The Mfgr cut sheet only says to provide electrical that meets local codes. Says nothing else other than power requirements of 48-52 amps. 240V

The unit is manufactured in Australia and marketed through a Company in the U.S.

Because it’s in the unfinished basement space is that what would be requiring the GFCI protection if it does.

Thank you.
 
The ones I have done the wiring came thru the wall where the sauna was sitting and the unit was under the bench, The wire went directly into a disconnect and from there flex would be fine. I believe nm or se would be compliant also.
 
Sealtite sounds like a good option for the disco into the unit. Could reduce down to 8 THHN to get the 50 amp rating and make the termination a bit easier in the ridiculously small termination box.

So then no GFCI protection required or would that be an AHJ call?

Thanks
 
Sealtite sounds like a good option for the disco into the unit. Could reduce down to 8 THHN to get the 50 amp rating and make the termination a bit easier in the ridiculously small termination box.

So then no GFCI protection required or would that be an AHJ call?

Thanks
Its not required.
If it were my sauna I'd put it on a GFPE breaker.
 