Be careful of HOW this calculation is done. Every SCCR calculation uses some assumptions. For instance the infinite bus assumption doesn’t model the real (not infinite) source well nor cable impedances nor the effect of loads. So it is usually lower but could be higher! ANSI and some IEC methods handle inductive sources and sources but tend to underestimate cable impedances by assuming only inductance matters and not resistance.
The point by point method is suitable for spreadsheets and relatively simple for mere mortals, not just engineers with overpriced software.
Not sure if this was directed at me, or just put out there so that anybody viewing this thread gets the message, but above I outlined at how I'm arriving at these SCCA values. See below.
Past my edit time for the above, but wanted to add that the short circuit current I'm using for the utility feeder is not infinite bus (utility provided based off of their ASPEN model). All SCCAs in our system have been found using EasyPower. So little doubt about the accuracy.
EasyPower defaults to ANSI methods, but they provide a couple other calculation methods for finding SCCA.
OSHA regulations need to be met all the time. So if your equipment is overdutied, you are in violation of OSHA 1910.303.
I am not sure if you are using the infinite bus short circuit current which is typically provided by the utility and based on your wording, " We had our SCCA increase due to upgrades performed by the utility on their system. Unfortunately, original engineers designed for the SCCA that existed at the time, despite the size/impedance of the utility transformer having the potential for a much higher SCCA. " This would seem to indicate infinite bus. If it is, you should get the available short circuit current from the utility. You may find that your equipment is not overdutied using the available short circuit current.
You do not specify what type of equipment is overdutied but if panels/breakers there may be series ratings that can help.
After re-reading my post, I could see how that may be interpreted as using infinite bus. Just to be clear, the utility increased wire size to provide a neighbor of ours with increased capacity. This led to an increase in SCCA at our equipment which caused it to become inadequate (still short of infinite bus, but enough to become a problem).
This is a good learning experience for anyone working on 5-year Arc Flash revalidation that you should always contact the utility to get the most up-to-date value. In my case, I saw them changing out the wire, so I knew that I should ask the question immediately.
You don’t need a regulation to tell you that overdutied equipment is a bad idea. It is very common to see drives blown up when a motor goes to ground, contactors welded shut or turned to slag, and breakers similarly obliterated when a fault occurs far worse than the damage of the fault itself. Bus bars turned into art work as they bend and rip loose from the insulators is impressive but less common. It’s not like it won’t trip and burn down a building but the damage is much more immediate.
And if you think there is some wiggle room think again! SCCR is not like thermal damage. Effects are proportional to the square of the current so a small amount under is much more severe than expected.
You paint a vivid picture, and no doubt I'll be doing the same. However, if you're staring down the barrel of a million dollar mitigation project, it's best to show up with all the facts in place, is it not? The safety implications are justification enough in my mind, just want to have the full story when I present the information.
There's been a lot of great info in this thread, but the original intent was to chase down any specific regulations that apply to this situation.
I know that this is primarily an NEC forum, but the NEC is an installation code, and in this particular case we aren't changing anything. The equipment became underrated by actions performed by the utility, so it would seem to me that the NEC doesn't apply to this particular situation.