wbdvt
Senior Member
- Location
- Rutland, VT, USA
- Occupation
- Electrical Engineer, PE
All the CL for a fuse is based on the fault current that it is seeing. So far the conversation seems to be centered on a bolted fault current and determining the let thru based on that. But what if it is an arcing fault current that is less than the bolted fault current but not in the current limiting range of the fuse and results in a fault current greater than the SCCR of the equipment?