necnotevenclose
Senior Member
When equipment is ordered and installed with an incorrect nameplate it causes several issues. When those issues come up, the equipment manufacture usually looks to electrical to provide a solution. Depending on your AHJ, that electrical solution may prohibit you to use current limiting fuses. When this has come up, a 3rd party testing agency has had to be hired to prove and relabel the equipment which delayed the C of O date and increased cost since components may need to get changed out. In my opinion this could be best avoided during design and ordering of the equipment.
With the changes of NEC and UL 1995 electrical inspectors are verifying more & more (its good thing) that the installed equipment (where required to comply with) is listed with a SCCR rating that meets or exceed the available fault current. I've been running more and more short circuit calcs to show what the calculated value at equipment, and even showing that information on plans. The problem is that information can still get looked over.
So my question is who is responsible for making sure the equipment that is ordered/installed has the appropriate SCCR rating?
Is it the GC, EC, MC, Elev. Contractor, Fire Protection Contractor, Electrical Engineer?
With the changes of NEC and UL 1995 electrical inspectors are verifying more & more (its good thing) that the installed equipment (where required to comply with) is listed with a SCCR rating that meets or exceed the available fault current. I've been running more and more short circuit calcs to show what the calculated value at equipment, and even showing that information on plans. The problem is that information can still get looked over.
So my question is who is responsible for making sure the equipment that is ordered/installed has the appropriate SCCR rating?
Is it the GC, EC, MC, Elev. Contractor, Fire Protection Contractor, Electrical Engineer?