SE cable

Status
Not open for further replies.

nickelec

Senior Member
Location
US
I never use Se cable here in NYC . Is this permitted this is out side on the load side of meter. Main service switch is located inside
32c03d997034dabfd3f5628e936c0a93.jpg
97187ee7ae4ba32c4f2d6004b1cbaa86.jpg
ab710ecf726d9b632999f6411c33bc40.jpg


Sent from my SM-S906U using Tapatalk
 
Yes it's permitted by the NEC. There are some limitations when installed in a raceway like fill (53%), above ground only, and 5X bend radius if installed in a conduit body.
 
I'm assuming you also need an approved connector. And this isn't acceptable
b64c894537b47c5847cf0d2be728e4a5.jpg
64c9dca0d8d9513b4edefd90639f4d90.jpg


Sent from my SM-S906U using Tapatalk
 