Hello - so we need to replace the sec due to it being frayed. There is a #4 copper coming from the footings to the panel.When I checked the water main I noticed that it had been changed to plastic. So my question is can I just add a ground rod to replace the one that went to the water pipe?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If there is a connection to a CEE in the footing an additional electrode is not required.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
CEE- concrete encased electrode.
As mentioned, if you have a CEE you do not need any additional grounding electrode.
See 250.52.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Just noticed you said "SEC" in your post. To most that means service entrance conductor. Do you mean GEC as in grounding electrode conductor?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Just noticed you said "SEC" in your post. To most that means service entrance conductor. Do you mean GEC as in grounding electrode conductor?

Sounds like he's changing the old SE cable and found that the water pipe electrode is no longer present because it's been changed to plastic. If the CEE exists then as you've stated no other electrodes are required to replace the water pipe electrode.
 