Jennifer K. said:
"Thank you for your responses! I wanted to add some additional information - the generator is outside of the building that it is serving; the feed from the generator goes to a generator distribution panel inside of the building (and the transfer switches are downstream from the generator distribution panel). The thought it to terminate the neutral at the GDP (distribution panel) and use 3 pole transfer switches. So I would like to know if this would be considered a separately derived system?"
"The thought it to terminate the neutral at the GDP (distribution panel) and use 3 pole transfer switches. So I would like to know if this would be considered a separately derived system?"
Jennifer K would still be wiring the GDP as a separately derived system.
And I would imagine the GDP has a main at the GDP.
Original thread:
"This would be for the case where the loads served from the generator do not require a neutral at the present time"