separately derived system

Status
Not open for further replies.

jbolen

Senior Member
We have 480 Delta Service. To feed the lighting we installed a Delta / Y transformer 480 to 480/277 4 wire. The question on job site is where the Grounding electrode conductor is terminated on both ends?
We are not allowed to drill holes in the steel structure at this location but Main Grounding Bar is 50 feet from transformer.

Ground Ring is Cald welded to the steel structure.
 

david

Senior Member
Location
Pennsylvania
The question on job site is where the Grounding electrode conductor is terminated on both ends?


Ground Ring is Cald welded to the steel structure.

To the closes grounding electrode near the SDS i

Normally in the transformer or in the panel for the 480/277 distribution
 

victor.cherkashi

Senior Member
Location
NYC, NY
"Main Grounding Bar is 50 feet from transformer" is not the same as grounding electrode. take a look at 250.30(A)(5) and 250.30(A)(5)

Sent from my ONEPLUS A6013 using Tapatalk
 