jwelectric
Senior Member
- Location
- North Carolina
I have not read all eight pages of this thread and being that this has been hashed to death so many times before I have no desire to read all eight pages.
I am posting ONLY because of what George said here and this comment.
The NEC is not silent on this matter and is very clear on the proper installation of SE-U and SE-R cable when these cables are being used as anything other than Service Entrance Conductors.
338.10(B)(4)(b) is the proper installation of SE-U and SE-R cable when these cables are being installed outside. I don’t think that anyone in this forum would dispute that underground is outside.
Part I of 225 is dealing with overhead conductors and Part II of 396 is dealing with the installation of conductors that are supported by a messenger wire and I don’t see a messenger wire being installed in conduit underground.
Now get that SE cable out of the pipe and install something that the NEC will allow to be installed in the underground pipe!
George I will post again if I see that this thread has a chance of making 300 or even the all elusive 1000 post thread.
EDDITED TO ADD
George
A basement is part of the interior of a building and not the exterior as being discussed.
I am posting ONLY because of what George said here and this comment.
The NEC is not silent on this matter and is very clear on the proper installation of SE-U and SE-R cable when these cables are being used as anything other than Service Entrance Conductors.
338.10(B)(4)(b) is the proper installation of SE-U and SE-R cable when these cables are being installed outside. I don’t think that anyone in this forum would dispute that underground is outside.
NEC said:(b) Exterior Installations. In addition to the provisions of this article, service-entrance cable used for feeders or branch circuits, where installed as exterior wiring, shall be installed in accordance with Part I of Article 225. The cable shall be supported in accordance with 334.30, unless used as messenger-supported wiring as permitted in Part II of Article 396.
NEC said:(this is for underground installations.)
Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340. Where Type USE cable emerges from the ground at terminations, it shall be protected in accordance with 300.5(D).
Multiconductor service-entrance cable shall be permitted to be installed as messenger-supported wiring in accordance with 225.10 and Part II of Article 396.
Part I of 225 is dealing with overhead conductors and Part II of 396 is dealing with the installation of conductors that are supported by a messenger wire and I don’t see a messenger wire being installed in conduit underground.
Now get that SE cable out of the pipe and install something that the NEC will allow to be installed in the underground pipe!
George I will post again if I see that this thread has a chance of making 300 or even the all elusive 1000 post thread.
EDDITED TO ADD
George
A basement is part of the interior of a building and not the exterior as being discussed.
Last edited: