Sorry but what is svc?
Abbreviation for SerViCe.
Sorry but what is svc?
My question is really several parts:
1a. What's the smallest al SER we can use one 200 breaker on (200a svc)?
1b. What's the smallest al SER we can use two 200a breakers on (320a svc)?
2a. What's the largest breaker we can use to protect one 4/0 al SER (200a svc)?
2b. What's the largest breakers we can use to protect two 4/0 al SER's (320a svc)?
Unfortunately it is going to depend on what Code cycle in use and how the AHJ enforces the "60? rule"
Also it will depend on if you ask Gus or you ask Dennis. :grin:
And Gus is/was an inspector. :grin:Not to the inspector. :grin:
isAnd Gus is/was an inspector. :grin:
'05 here in Va.Unfortunately it is going to depend on what Code cycle in use and how the AHJ enforces the "60? rule"
Yes.assuming we are speaking of installs which fit the terms of 310.15(b)(6)
Which is NEC, 'local' or 'many'?1a.
Locally: With interior SER, 300 kcmil AL, 4/0 Cu
Most areas: 4/0 AL, 2/0 Cu
1b. Based on 2 cables to 2 200 amp panles
Locally and some areas: 300 kcmil AL, 4/0 Cu
Some areas: 4/0 AL, 2/0 Cu
2a. Locally with interior runs 150 amp (on Al)
Most areas 200 amp
2b Locally with interior runs 150 amp (on AL)
many areas 200 amp
In the "200a svc" cases, yes, in the "320a svc" cases, no.Larry I am confused your questions are mentioning service but you state ser. Do you mean when the ser carries the entire load?
'05 here in Va.
Yes.
Which is NEC, 'local' or 'many'?![]()
I have been, believe me.You can do a search of "338.10" and follow the points of view.
The best bet is to ask the inspector about any subject that's known to be less than clear, but, that can be a double-edged sword: it's good to know before you start, but bad to alert him to a new change we've lived without in our blissful 'ignorance'.... "Code" on this particular subject is much an interpretation by the AHJ in that particular area.
Just to clarify one thing. Let's say you are doing an overhead service on a single family home. You run #2 SE down the wall and hit the meter socket, then out of meter into home but the loadcenter location on the oppisite side of unfinished basement so you install a disconnect right below the meter socket on the OUTSIDE of home. Now we have to run subfeed cable to across the basement to the subpanel.
Can you still run the #2 al subfeed since this is considered service entrance and not branch circuit or feeder?