It will solve nothing , and I fear we will not resolve the problem here in the Forum, but since it's been a long while, this is the reasoning prersented by a member of CMP1
"215.2 and 310.15(B)(6) are what they are. 310.15(B)(6) allows a "rating" of 200 amperes for 4/0 aluminum conductors. This "rating" is not an allowable ampacity such as is provided in Table 310.16 but is
what it is - just a rating. Therefore, again, everything being equal
215.2(A)(3) states that "Feeder conductors for individual dwelling units or mobile homes need not be larger than service conductors." However, we are not equal where SE cable is utilized as the feeder wiring method to the secondary distribution panelboard inside the dwelling. See
338.10(B)(4)(a) that states "a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334." Note that the exclusion of 334.80 per the 2005 NEC is not excluded in the 2008 NEC in this section. This is because the code panel believes that SE cable is susceptible to having the same conductor heat dissipation problems as NM cable when run in the interior of buildings in attics and walls and especially where such cable is embedded in insulation. Therefore, 4/0 aluminum SE cable has to be sized from the 60-degree ampacity column of Table 310.16 which only allows it to have an allowable ampacity of 150 amps. Therefore, if the calculated load is 180 amps the 4/0 aluminum cable would not be acceptable and a 300 kcmil aluminum conductor at 190 amperes' would be
required per Table 310.16. Again, all things are not equal between the
service on the exterior of the dwelling and the feeder run through the interior of the dwelling
"215.2 and 310.15(B)(6) are what they are. 310.15(B)(6) allows a "rating" of 200 amperes for 4/0 aluminum conductors. This "rating" is not an allowable ampacity such as is provided in Table 310.16 but is
what it is - just a rating. Therefore, again, everything being equal
215.2(A)(3) states that "Feeder conductors for individual dwelling units or mobile homes need not be larger than service conductors." However, we are not equal where SE cable is utilized as the feeder wiring method to the secondary distribution panelboard inside the dwelling. See
338.10(B)(4)(a) that states "a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334." Note that the exclusion of 334.80 per the 2005 NEC is not excluded in the 2008 NEC in this section. This is because the code panel believes that SE cable is susceptible to having the same conductor heat dissipation problems as NM cable when run in the interior of buildings in attics and walls and especially where such cable is embedded in insulation. Therefore, 4/0 aluminum SE cable has to be sized from the 60-degree ampacity column of Table 310.16 which only allows it to have an allowable ampacity of 150 amps. Therefore, if the calculated load is 180 amps the 4/0 aluminum cable would not be acceptable and a 300 kcmil aluminum conductor at 190 amperes' would be
required per Table 310.16. Again, all things are not equal between the
service on the exterior of the dwelling and the feeder run through the interior of the dwelling