I have an inspector telling me that service conductors can NEVER be inside a building and he quotes NEC (or rather CEC, but same thing) 230.6 item (2) as his justification
230.6 Conductors Considered Outside the Building.
Conductors shall be considered outside of a building orother structure under any of the following conditions:
...
(2) Where installed within a building or other structure in araceway that is encased in concrete or brick not lessthan 50 mm (2 in.) thick
I say its clear that he is misinterpreting that code. It does not say that service conductors shall be outside of buildings but rather that they can be considered as being outside a building if encased in concrete. If you read the preceding section, 230.3, its clear that 230.6, among other things, is a remedy for the situation mention in 230.3
230.3 One Building or Other Structure Not to Be SuppliedThrough Another.
Service conductors supplying abuilding or other structure shall not pass through the interiorof another building or other structure
Let me explain the situation. I'm dealing with a new overhead service installation. New flush mount meter panel on a garage wall 5 feet away from the original meter panel location. For reasons that would take a long time to explain I had to stub the mast up out of the roof 4 feet away horizontally from the new meter panel location. I ran the mast through the garage wall by putting a ninety out the top of the panel to a short length of pipe to another ninety pointing up to a 5 foot piece of pipe stubbed out of the roof. He says the service conductors are inside the building (which they are) and that that violates code. I asked him what about a completely vertical mast inside the wall straight up out of the panel and out of the roof (which is admittedly how most flush mount overhead services are done). He said that in that case the conductors would not be considered as being inside the building but once they run horizontal they are then considered to be inside. I know there is no basis for that distinction in the code.
I have other reasons explaining why I think he's wrong but I'd like to hear from the forum what they think.
230.6 Conductors Considered Outside the Building.
Conductors shall be considered outside of a building orother structure under any of the following conditions:
...
(2) Where installed within a building or other structure in araceway that is encased in concrete or brick not lessthan 50 mm (2 in.) thick
I say its clear that he is misinterpreting that code. It does not say that service conductors shall be outside of buildings but rather that they can be considered as being outside a building if encased in concrete. If you read the preceding section, 230.3, its clear that 230.6, among other things, is a remedy for the situation mention in 230.3
230.3 One Building or Other Structure Not to Be SuppliedThrough Another.
Service conductors supplying abuilding or other structure shall not pass through the interiorof another building or other structure
Let me explain the situation. I'm dealing with a new overhead service installation. New flush mount meter panel on a garage wall 5 feet away from the original meter panel location. For reasons that would take a long time to explain I had to stub the mast up out of the roof 4 feet away horizontally from the new meter panel location. I ran the mast through the garage wall by putting a ninety out the top of the panel to a short length of pipe to another ninety pointing up to a 5 foot piece of pipe stubbed out of the roof. He says the service conductors are inside the building (which they are) and that that violates code. I asked him what about a completely vertical mast inside the wall straight up out of the panel and out of the roof (which is admittedly how most flush mount overhead services are done). He said that in that case the conductors would not be considered as being inside the building but once they run horizontal they are then considered to be inside. I know there is no basis for that distinction in the code.
I have other reasons explaining why I think he's wrong but I'd like to hear from the forum what they think.