I have posted a thread on this topic previously where I was trying to design a circuit to feed a transformer and panel and I got a lot of help and suggestions with some of the design and code aspects. I thank everyone who contributed.
I have now come up with what I think is a final design and wanted to bounce it off some of you guys.
Basically the scope of the project is to have a 100A 120/240 panel at a remote location. The distance from the closest power source is aproximately 1200ft. The following is my ciruict and design choices.
1) 70A 480V Feeder Breaker Located in 480V MCC
|
|
|
2) 1200 ft of 3/c #2 AWG (To account for voltage drop)
|
|
|
3) 70A Disconnect (Unfused) located at remote location (MaintananceShutoff)
|
|
|
4) 25kVA 480-120/240 Outdoor Transformer
|
|
|
5) 100A 120/240 panel located right next to transformer (5ft) with a 100A
Main breaker in panel.
What do you guys think of this final design? Does it meet code? Good design choices?