service disconnect location

Status
Not open for further replies.
Never had a problem with IPL, Cinergy or Hendricks on the load side.....Charlie I am formally from In. What is the distance now? DC just changed from 15' to Nearest the point of entrance which is exactly what it means and all are on the same page here.....back to back....Funny how AHJ's look at things such as this.
What did I do now :grin:
 
The wording "nearest the point of entrance" could be distorted to mean place the main panelboard at the ceiling height and build something to climb up to this location while still meeting 110-26 for clearances.
Where's the distortion? That sounds compliant. Not pretty, maybe.

Disco at ceiling height with permanent ladder, and ML panel below.
 
It remains my opinion that the word "nearest" means exactly that and you have to install the disconnect at the point where the service conductors penetrate the interior wall surface.

It remains my opinion that if the CMP meant what you believe that the wording would be "at the point of entrance" not "nearest the point of entrance" :smile:

The planet Mercury is 'nearest to the sun' but it is hardly 'at the sun'. :smile:
 
It remains my opinion that if the CMP meant what you believe that the wording would be "at the point of entrance" not "nearest the point of entrance" :smile:

The planet Mercury is 'nearest to the sun' but it is hardly 'at the sun'. :smile:

Well good analogy but I feel "at" was a figure of speech. "The" as in Nearest the point .......Picky picky....but point made.
 
service disconnect location

It remains my opinion that if the CMP meant what you believe that the wording would be "at the point of entrance" not "nearest the point of entrance" :smile:

The planet Mercury is 'nearest to the sun' but it is hardly 'at the sun'. :smile:

It amuses me to see how some try using the wording to try allowing the service main to be not at the point of entrance.

I really believe we understand that the intent is to keep the unprotected service conductors inside a dwelling to a minimum.IMO that is a good idea.

With that in mind in the interest of public safety I will continue to red tag any installations not at the point of entrance.
 
It amuses me to see how some try using the wording to try allowing the service main to be not at the point of entrance.

It amuses me that your answering the thread without really reading it, :D or that is what it seems.


I really believe we understand that the intent is to keep the unprotected service conductors inside a dwelling to a minimum.IMO that is a good idea.

No doubt, I agree.

With that in mind in the interest of public safety I will continue to red tag any installations not at the point of entrance.

Really? I don't think you do.

Don's point was that in his opinion the wording of the NEC allows no amount of service conductor to enter the building.

I would have to have come from outside the building directly into the back of the panel. Now as I am sure you are aware in MA that is not the case, most panels are in the basement and have 3' to 5' of service conductors coming in through the sill and down the basement wall into the top of panel. In Don's opinion the NEC directly prohibits that.

I am not at all suggesting I can run 30' into the building, only that I can run far enough to get into a panel that is located nearest the point of entrance not at the point of entrance. :smile:
 
The wording of 230.70(A)(1) addresses the disconnecting means.

It does not say much, except for alluding to, the SE conductors.
I, myself think that this section needs to be addressed. It was probably fine when first written, but now, like other code wording, has been disected and needs a little "massaging."

The CMP(s) responsible for this SE cable and service disconnecting means should further evaluate the wording.
Why?

Like other sections of the NEC that have been addressed when there is confusion in enforcement, this section is no different.

It would be interesting in the least to see how this wording could be worked on to ease the enforcement dilemas we see in the field.
 
service disconnect location

It amuses me that your answering the thread without really reading it, :D or that is what it seems.




No doubt, I agree.



Really? I don't think you do.

Don's point was that in his opinion the wording of the NEC allows no amount of service conductor to enter the building.

I would have to have come from outside the building directly into the back of the panel. Now as I am sure you are aware in MA that is not the case, most panels are in the basement and have 3' to 5' of service conductors coming in through the sill and down the basement wall into the top of panel. In Don's opinion the NEC directly prohibits that.

I am not at all suggesting I can run 30' into the building, only that I can run far enough to get into a panel that is located nearest the point of entrance not at the point of entrance. :smile:[/QUOTE

I doubt that is Dons point,if it is then I disagree with him. The 3ft. to 5ft. you suggest IMO is acceptable and code compliant as being at the nearest the point of enterance.
 
I, myself think that this section needs to be addressed. It was probably fine when first written, but now, like other code wording, has been disected and needs a little "massaging."

I respectfully ask why you feel that way?

Have you any evidence that as it is written today it is creating an electrical hazard?

Not trying to be a wise guy, I just personally do not like to see code changes without ample substantiation. :smile:

If we could point to a number of fires and or injuries directly as a result of letting a few feet of service conductors inside the building then I would say the NEC would need to address it.

California is a great example, they allow the RMC service riser to enter the building through the roof and down inside the wall all the way to the panel. One would have to imagine that after many years of allowing this if it was resulting in fires the powers that be would change the rules. Especially since CA seems quick to 'make a rule' needed or not.:smile:
 
I doubt that is Dons point,if it is then I disagree with him. The 3ft. to 5ft. you suggest IMO is acceptable and code compliant as being at the nearest the point of enterance.

I am hesitant to speak for Don, maybe he will jump back in but here is what he said in about the 5th or 6th post. :smile:


It remains my opinion that the word "nearest" means exactly that and you have to install the disconnect at the point where the service conductors penetrate the interior wall surface.
 