I understand that most code users read this section as if it had the words "as close as practical" in it, but I don't.
Nor do we here. Good post Don.
I understand that most code users read this section as if it had the words "as close as practical" in it, but I don't.
What did I do now :grin:Never had a problem with IPL, Cinergy or Hendricks on the load side.....Charlie I am formally from In. What is the distance now? DC just changed from 15' to Nearest the point of entrance which is exactly what it means and all are on the same page here.....back to back....Funny how AHJ's look at things such as this.
Where's the distortion? That sounds compliant. Not pretty, maybe.The wording "nearest the point of entrance" could be distorted to mean place the main panelboard at the ceiling height and build something to climb up to this location while still meeting 110-26 for clearances.
Where's the distortion? That sounds compliant. Not pretty, maybe.
Disco at ceiling height with permanent ladder, and ML panel below.
It remains my opinion that the word "nearest" means exactly that and you have to install the disconnect at the point where the service conductors penetrate the interior wall surface.
What did I do now :grin:
I wouldn't recommend doing it, but what's non-compliant about it?I don't see any "smilies" but I can only hope you're joking.![]()
So, in your solar system, Mercury would not require an exterior disconnect. :wink:The planet Mercury is 'nearest to the sun' but it is hardly 'at the sun'. :smile:
So, in your solar system, Mercury would not require an exterior disconnect. :wink:
It remains my opinion that if the CMP meant what you believe that the wording would be "at the point of entrance" not "nearest the point of entrance" :smile:
The planet Mercury is 'nearest to the sun' but it is hardly 'at the sun'. :smile:
And a separate EGC if under 2008+ NEC.Nope but any feeders to remote planets will have to have a disconnecting means.
Not to mention ambient-temperature derating.Voltage drop is a bear. :wink:
I have a strange feeling this thread will turn into a solar system thing now...:roll:
I can put the brakes on that. :smile:
It remains my opinion that if the CMP meant what you believe that the wording would be "at the point of entrance" not "nearest the point of entrance" :smile:
The planet Mercury is 'nearest to the sun' but it is hardly 'at the sun'. :smile:
It amuses me to see how some try using the wording to try allowing the service main to be not at the point of entrance.
I really believe we understand that the intent is to keep the unprotected service conductors inside a dwelling to a minimum.IMO that is a good idea.
With that in mind in the interest of public safety I will continue to red tag any installations not at the point of entrance.
It amuses me that your answering the thread without really reading it,or that is what it seems.
No doubt, I agree.
Really? I don't think you do.
Don's point was that in his opinion the wording of the NEC allows no amount of service conductor to enter the building.
I would have to have come from outside the building directly into the back of the panel. Now as I am sure you are aware in MA that is not the case, most panels are in the basement and have 3' to 5' of service conductors coming in through the sill and down the basement wall into the top of panel. In Don's opinion the NEC directly prohibits that.
I am not at all suggesting I can run 30' into the building, only that I can run far enough to get into a panel that is located nearest the point of entrance not at the point of entrance. :smile:[/QUOTE
I doubt that is Dons point,if it is then I disagree with him. The 3ft. to 5ft. you suggest IMO is acceptable and code compliant as being at the nearest the point of enterance.
I, myself think that this section needs to be addressed. It was probably fine when first written, but now, like other code wording, has been disected and needs a little "massaging."
I doubt that is Dons point,if it is then I disagree with him. The 3ft. to 5ft. you suggest IMO is acceptable and code compliant as being at the nearest the point of enterance.
It remains my opinion that the word "nearest" means exactly that and you have to install the disconnect at the point where the service conductors penetrate the interior wall surface.