Another option would be to present actual known data from a utility and show the 400 amp service is large enough for the existing load and the additional calculated load.
Those are both considered load calculations (220.87). So no, that wasn't the point back around post #31. I mean, you might find that 220.87 results in a load calc less than 400A, but you might even find that other methods do as well.I think the point is that if one looked at demand history and it were low enough it may be possible to add the new load to the existing 400 amps of service conductor, keep existing 400 amp main and add the additional 200 amp main.
Again, we don't know where the service point is, and it was unclear exactly what was being proposed. I see three scenarios.
1) The conductors coming into the existing 400A breaker are customer owned, and the total NEC load calculation exceeds their rating.
Option A: upgrade the existing customer owned conductors (multiple options for disconnects at the load end)
Option B: install a new set of service entrance conductors all the way back to the service point, wherever that is
2) The conductors coming into the existing 400A breaker are customer owned, and the total NEC load calculation does not exceed their rating.
Option A: Replace existing 400A equipment with 600A
Option B: Tap existing conductors to new 200A alongside existing 400A
Option C: install a new set of service entrance conductors all the way back to the service point, wherever that is
Note: none of these options requires upgrading the existing conductors
3) The conductors coming into the existing 400A breaker are utility owned.
It is up to the utility to decide if the existing conductors need to be upgraded, and they would ask for load information, although it may not need to be calculated according to the NEC.
So regardless of the scenario, some kind of load calculation is going to come into play if you want to know what all your compliant options are.