- Windsor, CO NEC: 2017
- Hospital Master Electrician
I disagree. Any metallic items can be bonded using the enclosure. I would agree if this is a neutral or a GEC as they cannot use the enclosure as a conductor.IMO, the 2nd setup would not be Code compliant. 250.80 states enclosures, & raceways shall be connected to the grounded conductor.
Your jumper from the enclosure to the nipples is dependent on the can to be the conductor.
That said, the second setup is terribly inefficient from a materials and labor stand point but I think compliant.
I will stand my ground. The wording of 250.80 vs 250.86 to me states service enclosures, etc,. have to be connected to the grounded conductor.
Non-service need only to be connected to equipment grounding means.
From a practical standpoint, depending on the service size, connecting all conduits in a loop can often require a jumper needing large lugs and more difficulty installing than installing an individual jumper to each conduit.
I think daisy chaining of grounded wire in the diagrams not a good idea:if upstream connexion broken, all downstream devices become ungrounded.
They tore out a legitimate install based on what the inspector MIGHT say.....?Everybody, and they tore out the first way to do it the second way for fear of what the inspector would say.
Yes. Iam against 'series' grounding'You're suggesting running an individual conductor to each of the eight raceways plus the CT can from the service neutral bus?
You went and had some edibles....?Now, imagine my response, when coupled with a rough week anyway.
Edit to add: tore out not once, but thrice.
I see your point and I am researchingaugie, lets see if we can hash this out. I'm agreeing with you, but only to a point as I stated in post #10. 250.80 says enclosures must be connected to the grounded conductor. 250 Part V Bonding tells you how you may accomplish this. As I stated, if it required a direct connection to the neutral conductor (such as a GEC would) there would be no use for, say, bonding type lock nuts used in a service application as permitted in 250.92.
I see your point and I am researching![]()
FWIW, 250.92 title is "Services".Only to a point
The specifics you have given are, IMO, listed in 250.92(B) (1),(2)(3) or (4).
I am not convinced (yet) that a conductor bolted (fastened) to the can is an approved method.
Working on it.![]()
...and a bonding-type locknut is one of the methods listed below.Electrical continuity at service equipment, service raceways, and service conductor enclosures shall be ensured by one of the following methods: