Service Grounding
IMO, the 2nd setup would not be Code compliant. 250.80 states enclosures, & raceways shall be connected to the grounded conductor.
Your jumper from the enclosure to the nipples is dependent on the can to be the conductor.
Okay, to attempt to defuse that a bit, allow me an edit:
I disagree. Any metallic items can be bonded using the enclosure. I would agree if this is a neutral or a GEC as they cannot use the enclosure as a conductor.
That said, the second setup is terribly inefficient from a materials and labor stand point but I think compliant.
I think daisy chaining of grounded wire in the diagrams not a good idea:if upstream connexion broken, all downstream devices become ungrounded.
I will stand my ground. The wording of 250.80 vs 250.86 to me states service enclosures, etc,. have to be connected to the grounded conductor.
Non-service need only to be connected to equipment grounding means.
From a practical standpoint, depending on the service size, connecting all conduits in a loop can often require a jumper needing large lugs and more difficulty installing than installing an individual jumper to each conduit.
Yes, I agree that enclosures, raceways, etc must be connected to the grounded conductor. I just don't think they must be directly connected. As an example, what if you were to bond the CT neutral to the can and bond the main disconnect neutral to the can and then use bonding type lock nuts for the nipples per 250.92. Routinely done, but by your interpretation this would violate 250.80. I do agree that a GEC would have to connect directly to the neutral bar.
And your point about daisy chaining the bonding jumpers is right on. I was thinking the same thing. The required size can get out of hand real quick on a service with larger and multiple service conductors.
You're suggesting running an individual conductor to each of the eight raceways plus the CT can from the service neutral bus?
augie, lets see if we can hash this out. I'm agreeing with you, but only to a point as I stated in post #10. 250.80 says enclosures must be connected to the grounded conductor. 250 Part V Bonding tells you how you may accomplish this. As I stated, if it required a direct connection to the neutral conductor (such as a GEC would) there would be no use for, say, bonding type lock nuts used in a service application as permitted in 250.92.
I see your point and I am researching :D
If I may, let me use another example. Assume a 3R enclosure with a service raceway entering the top thru a factory optional bolt on hub. How would you connect that raceway directly to the neutral/grounded conductor? You can't and don't need to as it is indirectly connected to the neutral in a manner compliant with 250.92.
Am I making my case?:D
Only to a point :D
The specifics you have given are, IMO, listed in 250.92(B) (1),(2)(3) or (4).
I am not convinced (yet) that a conductor bolted (fastened) to the can is an approved method.
Working on it. :)
Only to a point :D
Working on it. :)
FWIW, 250.92 title is "Services".
Also, within the the general statement of 250.92(B) is...
Electrical continuity at service equipment, service raceways, and service conductor enclosures shall be ensured by one of the following methods:
...and a bonding-type locknut is one of the methods listed below.
If a service raceway (or enclosure, depending on how you look at it) is permitted to be bonded using a bonding-type locknut, how would you connect it to the grounded conductor???