Is that an indoor recessed panel in an outside wall facing the outside? H'mm
Silly. Can't come up with a specific violation, though. Maybe lack of support within 3' of enclosure?
I believe the couplings and the hub is listed for rigid conduit. Now, is the offset considered rigid, I don't know.
The panel is not listed to have a hub in that location. It is in a area of factory ko's. No smooth rolled edge for the wire. No tapped screw holes there either.
How does the wording need to be in order to cite a listing violation? I think the wording from UL is pretty clear.1) I don't see any enforceable violation;
5) The UL White Book note simply was UL's way of saying 'we don't know.' It's a mighty big stretch to call that a listing 'violation.'
3) I suspect a 2" mast and 100-amp service is now required.
That definitely is not a WP panel. WP panels do not have factory ko's on top. WP panels have bushed opening in the center with raised tapped screw holes to attached the hub to. If you look at the left side of the hub, you will see about 1/4 of a ko exposed outside the hub. It is an indor panel with a flush cover. There are no factory indor panels with hub openings. For grounding purposes the fittings must be wrench tight. Yes, it does need straps.
How does the wording need to be in order to cite a listing violation? I think the wording from UL is pretty clear.
It would be a POCO requirement. Around my neck of the woods minimum riser size is 1.25" and I can get away with 1.25" on a 200Amp panel. But other local POCO require a minimum of 2" for a 200Amp panel.
SQUARE-D does have a water proof panel with KO on top. It all depends how you install it. It can be recessed in the wall (similar to the OP) or surface installed with a blank cover on top of the panel that hides the KO.
Maybe the strap is installed within 36" but it is out of the picture.
And you get two 2/0 and one 1/0 in a 11/4" conduit HOW?:?
It is not a knock out. It is a bushed hole in the center. It comes with a blank hub/cover or you install the required size conduit hub. WP panels are not recessed into the wall because the cover has a lip the wrapes around the panel on both sides, and bottom to keep the water out. The cover is hinged on top.
If it fits, it fits.
what do you mean how? sarcastically?