skoal7839 said:would a 100amp service be big enough for a 20kw furnace this would be the only load hooked up to it
mdshunk said:20,000 x 1.25 = 25,000. 100 amps is 24,000
bummer.
skoal7839 said:would a 100amp service be big enough for a 20kw furnace this would be the only load hooked up to it
Of course, this is presuming 240v 1ph.mdshunk said:20,000 x 1.25 = 25,000. 100 amps is 24,000
tryinghard said:Mule, Its for fixed electric space heating: 424.3(B) ?Fixed electric space heating equipment shall be considered continuous load.?
And 210.19(A)(1) with 210.20(A), for ?continuous loads? conductors and overcurrent protection is sized at 125% of the load.
Cold Fusion said:However, when one goes to (2002) 424.22(D), it appears to allow sizing the conductors at 100% of nameplate. (???). I've never understood why the difference in wording between the two articles.
cf
wirebender said:i believe nameplates take the 125% into account.
eds said:so if I have a furnace with a mca of 51 and a mop of 60 than I have to take 51 times a 125% which would require a run of 4/2g instead of 6/2g
eds said:so if I have a furnace with a mca of 51 and a mop of 60 than I have to take 51 times a 125% which would require a run of 4/2g instead of 6/2g