skoal7839 said:
would a 100amp service be big enough for a 20kw furnace this would be the only load hooked up to it

I'm sure you'll get better comments than mine, (Im a has been) but assuming single phase 240 looks like 83, PLUS the blower motor, maybe 1/2 or 3/4hp I'd say your over, or hanging on a thread and a prayer. Besides cracking open the code book, look for the data plate, most HVAC equip has a min circuit amps posted
 
Mule, Its for fixed electric space heating: 424.3(B) ?Fixed electric space heating equipment shall be considered continuous load.?

And 210.19(A)(1) with 210.20(A), for ?continuous loads? conductors and overcurrent protection is sized at 125% of the load.
 
skoal7839 said:
would a 100amp service be big enough for a 20kw furnace this would be the only load hooked up to it

Let's assume you mean feeder not service. In either case, it won't fly, however many 20 kw furnace are only 19.2 kw. It may fly as a feeder. I would check the nameplate since you must also consider the fan in the calculation.
 
tryinghard said:
Mule, Its for fixed electric space heating: 424.3(B) ?Fixed electric space heating equipment shall be considered continuous load.?

And 210.19(A)(1) with 210.20(A), for ?continuous loads? conductors and overcurrent protection is sized at 125% of the load.

However, when one goes to (2002) 424.22(D), it appears to allow sizing the conductors at 100% of nameplate. (???). I've never understood why the difference in wording between the two articles.

cf
 
Cold Fusion said:
However, when one goes to (2002) 424.22(D), it appears to allow sizing the conductors at 100% of nameplate. (???). I've never understood why the difference in wording between the two articles.

cf

This is in 05 as well but it?s for "supplemental overcurrent protection", additional to the required.

Notice definition of Supplementary Overcurrent Protective Device: ??This limited protection is in addition to the protection provided in the required branch circuit by the branch circuit overcurrent protective device.?
 
so if I have a furnace with a mca of 51 and a mop of 60 than I have to take 51 times a 125% which would require a run of 4/2g instead of 6/2g
 
eds said:
so if I have a furnace with a mca of 51 and a mop of 60 than I have to take 51 times a 125% which would require a run of 4/2g instead of 6/2g

No- I don't think so -- the 125% is in there already.
 
acording to post #12 and the code sections mentioned do we know that this is already taken into account
 